    The NEC covers appliance wiring as well. Stranded wire is usually more flexible than its solid counterpart. This is especially helpful when pulling it through conduit and when used as flexible cord. The type of insulation will have a big influence on the stiffness and overall diameter of the conductor.

    It's been awhile but I believe (in part anyway) that appliance cord gets to be smaller than the circuit conductors because it is going to feed a dedicated load with a given, certain amount of load. (Think tap rule too). The one requirement I remember the NEC has is the cord has enough ampacity so that if it were to get damaged and the conductors short together, it could cause the breaker's instantaneous trip function to operate correctly. Take a lamp cord for example, it's much more likely for you to mash the cord (a short out the conductors and cause a short circuit than it is for you to load it up to twenty or more amps.

    Got a reference for this?

    Just noodling it - but you'd have to have really thin wire such that the resistance is high enough that it would not trip, roughly 8 ohms - something like 28 gauge wire (i.e. cat 5) for a ten foot stub that's shorted.

    15 amps through 28 ga. .... yeah, that's not going to last long.

    That said, I don't think I've seen many cords with 20 ga. or smaller.


    Anyways, when sizing cables for widgets, the primary concern is going to be physical robustness and how much does it heat up when powered. That's what UL tests - attach a thermocouple, run the device at max ambient temp and ensure the cable doesn't exceed the rating.
     

    GodFearinGunTotin

    Super Moderator
    Staff member
    Moderator
    Site Supporter
    Rating - 100%
    1   0   0
    Mar 22, 2011
    50,898
    113
    Mitchell
    Not right now. I don't have a code book handy right now.

    A regular circuit breaker has two trip modes: overload and short circuit. Even though they have no intentional delay for short circuit trips, the conductor has to be able to handle the magnitude of short circuit current until the breaker can clear the fault without burning up. A conductor may be rated for 20 amps let's say but it will conduct much more than that for limited amounts of time. Manufacturers know how long their lamp cords will carry typical fault currents found in residential applications.

    Got a reference for this?

    Just noodling it - but you'd have to have really thin wire such that the resistance is high enough that it would not trip, roughly 8 ohms - something like 28 gauge wire (i.e. cat 5) for a ten foot stub that's shorted.

    15 amps through 28 ga. .... yeah, that's not going to last long.

    That said, I don't think I've seen many cords with 20 ga. or smaller.


    Anyways, when sizing cables for widgets, the primary concern is going to be physical robustness and how much does it heat up when powered. That's what UL tests - attach a thermocouple, run the device at max ambient temp and ensure the cable doesn't exceed the rating.
     